Bottom of Overfill Flapper Valve fell into tank

UST, service station, bulk plant, car wash, commercial refueling installation, design and construction.
Post Reply
MarkWallace
Pump Jockey
Posts: 16
Joined: Thu Sep 13, 2007 9:11 am

Bottom of Overfill Flapper Valve fell into tank

Post by MarkWallace » Wed May 16, 2018 11:56 am

My Tech was removing an overfill flapper valve/drop tube from a tank (for the "new inspection/testing regulations") fill pipe. The top 1/2 of the flapper valve came out, but the bottom 1/2 fell into the tank. Any concerns with leaving the drop tube laying on the bottom of the tank?

Anyone else had this happen to them?

MWallace

hardworking
Head Tech
Posts: 40
Joined: Mon Sep 27, 2004 8:49 am

Re: Bottom of Overfill Flapper Valve fell into tank

Post by hardworking » Fri May 25, 2018 8:47 am

I don't think I would lose sleep over it. If you don't have a manway you don't have much of a choice.

hardworking
Head Tech
Posts: 40
Joined: Mon Sep 27, 2004 8:49 am

Re: Bottom of Overfill Flapper Valve fell into tank

Post by hardworking » Fri May 25, 2018 8:49 am

Although, it could mess with the floats on the tank gauge. Odds are it won't, but Murphy has a way.

fattermonk
Pump Jockey
Posts: 11
Joined: Mon Apr 09, 2018 10:10 am

Re: Bottom of Overfill Flapper Valve fell into tank

Post by fattermonk » Thu May 31, 2018 11:03 am

“If you ever drop your keys into a river of molten lava, let'em go...because man, they're gone!”

― Jack Handy

KellyVag
Newbie
Posts: 1
Joined: Mon Dec 03, 2018 4:39 am

Bottom of Overfill Flapper Valve fell into tank

Post by KellyVag » Thu Dec 06, 2018 4:14 pm

Just curious - when the suction fitting is at the top of the tank, is there a stand tube from the fitting down to the bottom of the tank?

Ken


ZMiller
Head Tech
Posts: 897
Joined: Sun Jul 15, 2007 10:53 am
Location: Atlanta/Phoenix/Sacramento

Re: Bottom of Overfill Flapper Valve fell into tank

Post by ZMiller » Fri Dec 07, 2018 9:57 am

A stinger runs from the top to the bottom of the tank. Older suction site stingers may have a "foot" check valve as well. What one sees on top of the tank looks kind of like an ball check extraction fitting. The 2" stinger NPT attaches to a NPT 2.5 or 3-inch extraction bell reducer or bushing and a cross bar extraction tool is typically required. Most are rotted off however and it becomes difficult to remove or replace. Finding the tank top fitting can be difficult as well as most access points have been paved or concreted over.
When you are dead it's likely you won't know it. It could be difficult for others. It's the same if you are stupid.
"Tact is the ability to tell someone to go to Hell in a way that they will begin looking forward to the trip"

dam5000
Newbie
Posts: 4
Joined: Tue Feb 27, 2018 10:27 pm

Re: Bottom of Overfill Flapper Valve fell into tank

Post by dam5000 » Fri Mar 08, 2019 4:54 pm

Had a Call out from a delivery driver that an over fill looked a little weird, when I arrived on site the bottom half was just hanging on by one screw. Undoing the fill collar was enough for the bottom half to fall into the tank. This was 4 years ago and still have had no issues arise . This tank was equipped with a TLM and STPs as well.