Search found 206 matches
- Tue Jul 02, 2019 5:38 am
- Forum: Service & Technical
- Topic: Advantage Door
- Replies: 5
- Views: 668
Re: Advantage Door
1/4" 20 x 2"
- Wed May 15, 2019 10:20 am
- Forum: Service & Technical
- Topic: EMC WPLLD Comm Alarm
- Replies: 9
- Views: 1127
Re: EMC WPLLD Comm Alarm
The WPLLD module subtracts a reference voltage from the voltage on the line to the STP. In a perfect world that subtraction cancels out AC voltage and leaves nothing but the signal from the pressure transducer. If there is noise on either the reference side or the STP side that won't cancel out and ...
- Thu May 02, 2019 5:59 am
- Forum: Service & Technical
- Topic: 2 Wire Conversion options for EMV
- Replies: 15
- Views: 3654
Re: 2 Wire Conversion options for EMV
There's no technical reason why any system that converts back and forth from TCP/IP to any form of communication capable of traveling over 2 wires can't be used. Communication is encrypted between pay at pump and network so security shouldn't be an issue either. That said, anyone doing an EMV audit ...
- Thu May 02, 2019 5:41 am
- Forum: Service & Technical
- Topic: 262 Programming Manual needed
- Replies: 11
- Views: 3622
Re: 262 Programming Manual needed
F00 Enter level 1 security code (If no security code is set F00 will be skipped and programming will begin at F02 F01 Set 2 digit arming code. If 00 is used just tap button if 0x is used 1 button code F02 Dollar Totals 2 decimal places eg. 1485.22 F03 Volume Totals 1 decimal place eg. 14852.2 If Lev...
- Fri Apr 05, 2019 5:43 am
- Forum: Service & Technical
- Topic: Encore 300 stuck at ATC error 104 on boot up
- Replies: 3
- Views: 506
Re: Encore 300 stuck at ATC error 104 on boot up
T-meter to IS barrier cable or the IS barrier
- Sat Mar 23, 2019 6:35 am
- Forum: Service & Technical
- Topic: Better of the 3 POS options?
- Replies: 17
- Views: 2489
Re: Better of the 3 POS options?
The 3 systems you are looking at all grew out of pump control and wet stock management. C-store was an add on. None of them are particularly friendly to use for managing store inventory in a stand alone configuration without a back office system, which adds expense. There are lots of systems around ...
- Fri Mar 22, 2019 5:30 am
- Forum: Service & Technical
- Topic: Better of the 3 POS options?
- Replies: 17
- Views: 2489
Re: Better of the 3 POS options?
If they are mainly selling fuel your best bet is probably a dedicated fuel controller like a Picon2 or TMS, then use whatever card processor will give you the best deal on equipment and fees.
A dedicated console is going to be roughly 1/5 the cost of an integrated POS and is probably all they need.
A dedicated console is going to be roughly 1/5 the cost of an integrated POS and is probably all they need.
- Thu Jan 17, 2019 2:30 pm
- Forum: Service & Technical
- Topic: Generator Load
- Replies: 7
- Views: 1068
Re: Generator Load
Have your electrician break out his clamp on ammeter and measure the actual draw at your site for the various devices. Once the cover is off the panel it will only take 10 minutes to measure the current draw for all your devices. Real world numbers beat theoretical any day. Remember that turbines dr...
- Tue Dec 18, 2018 10:14 am
- Forum: Service & Technical
- Topic: Encore 500
- Replies: 8
- Views: 1041
Re: Encore 500
CC77 to change pass codes, CC28 is only for level 1
There is no PCI requirement to change dispenser codes. Dispensers do not collect, store or transmit any payment information.
There is no PCI requirement to change dispenser codes. Dispensers do not collect, store or transmit any payment information.
- Fri Oct 26, 2018 8:07 am
- Forum: Service & Technical
- Topic: Problems with TLS4B and TLS RF
- Replies: 8
- Views: 1175
Re: Problems with TLS4B and TLS RF
Double check the polarity of the wiring from the RF box to the TLS,+ goes to + and - goes to -. Make sure that your RF box stays powered up when you reboot the TLS to put it in discovery mode.